    What is correct set up for an isolated ground system for computer plugs ? How do you set it up in the panel ? I was shown a way to do it but I am not convinced it's right. Can someone out there help me?

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    The insulated bonding (isolated ground) conductors can be kept isolated from the equipment enclosures back to the main distribution panel, but no farther. 10-906 (8)

    Ed

    Example-
    IsolGnd

  3. #3
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Question

    Ed: What do you do if the service is 600V, do you still bring the I.G. back to the main distribution panel, or can you bring the I.G. back to the X0 of the 600-120/208V transformer?

    <font color="#a62a2a" size="1">[ January 13, 2004 09:59 PM: Message edited by: ccrash ]</font>

  4. #4
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Yes, as you suggested, you bring the I.G. back to the X0 of the 600-120/208V transformer?

    The basic principle is that you can keep them isolated back to the point where their supply system's grounding electrode conductor and equipment bonding conductors are connected to the system's neutral.

    Ed

  5. #5
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Thanks Ed.